hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have incoming utility feeds into CUSTOMER owned transformer. The transformer secondary conductors feed to fire pump and switchboard. The secondary conductor come into switchboard and on separate vertical section the line side is tapped and from switchboard separate compartment tap line side go into building to 100 feet away to first disco means and another 10 feet to fire pump controller and to fire pump.
I have inspector telling me that I need to place conductors from the switchboard tap to the LINE side of fire pump first disconnecting means in concerte encased min 2 in thick. 100 feet of cables.
I looked at NEC 2014 and did not find anything. Anything that comes close is 695.6(A)(2) but it says conductors on load side of first disco but inspector is requiring from tap to line side first disco.
I do not know where inspector is getting this. Which code article section would apply?
I have inspector telling me that I need to place conductors from the switchboard tap to the LINE side of fire pump first disconnecting means in concerte encased min 2 in thick. 100 feet of cables.
I looked at NEC 2014 and did not find anything. Anything that comes close is 695.6(A)(2) but it says conductors on load side of first disco but inspector is requiring from tap to line side first disco.
I do not know where inspector is getting this. Which code article section would apply?