1) I was told that when it comes to A/C condensers the 125% motor calculation does not apply. Instead you should just go by it's max ampere rating. So if it's 35a max load, you should size the circuit for 40a. If it's a 40amp max load, you should size the circuit for 40a also. Is this correct?
- if yes, is the continuous load calculation already taken into consideration with these numbers?
2) On the subject, i'm a little bit cloudy on the motor calculations in general. If you have an air compressor rated at 37a:
37a x 1.25 = 46.25a
So, size the circuit for 50a. Is this correct?
- and if it will be running for 3 hours or more what is the continuous load calculation and how does it apply in this example?
3)Is this the proper way to size circuits for all motors other than A/C condensers?
- what is the max allowable voltage drop on a motor circuit?
Thanks guys.
- if yes, is the continuous load calculation already taken into consideration with these numbers?
2) On the subject, i'm a little bit cloudy on the motor calculations in general. If you have an air compressor rated at 37a:
37a x 1.25 = 46.25a
So, size the circuit for 50a. Is this correct?
- and if it will be running for 3 hours or more what is the continuous load calculation and how does it apply in this example?
3)Is this the proper way to size circuits for all motors other than A/C condensers?
- what is the max allowable voltage drop on a motor circuit?
Thanks guys.