Condenser Units Panel

Status
Not open for further replies.

blues

Member
Location
Nevada
I have a project where the mechanical supplier plans to provide (3) condensing units on a skid with a pre-wire control panel with breakers for each unit. I am not sure how to size the feeder to this panel. My first thought is to take the MCA for each and use that sum for the amperage of my feeder conductors to the PWCP. Any thoughts or comment are always appreciated.

Dan Craven
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Adding the 3-MCA's will probably give a number larger than necessary. Does the unit have a single MCA for the entire package?
 