Condensing Unit Breaker Size

Status
Not open for further replies.

Electricalhelp

Senior Member
Location
NJ
Do I only need a 15 AMP/208V/1P Breaker for the Condensing Unit


Because it also list the Compressor LRA at 41 Amp.

See attached Label
 

Attachments

  • IMG_2820.jpg
    IMG_2820.jpg
    69.3 KB · Views: 17
Do I only need a 15 AMP/208V/1P Breaker for the Condensing Unit


Because it also list the Compressor LRA at 41 Amp.

See attached Label

Follow the manufacturer's recommendations ... The work is already done for you.

This always trip people up ... the compressors are cooled by the suction line return and don't pull as much amps as standard motors. A hermetic compressor is a sealed unit with compressor and motor together.
 
The label has the Minimum Circuit Ampacity (MCA) and max breaker sizes specified. That is all you need. Since it is 208V, it would be a 2 pole 15A breaker.

The Locked Rotor Amps LRA is rarely used except when checking the size of a generator or transformer feeding the service or feeder.
 
No. However, the power company may ask what your highest LRA motor is when selecting the transformer to feed that service (the transformer needs to be large enough to supply that LRA). Or if it an industrial site and you have your own transformers and distribution, you'd need to look at transformer size when there are larger motor loads.
 