Condensing Unit disconnect
Stevedallas
Dallas, TX
Engineer
I know 440 requires a disconnecting means. But, does it need to be fused?
I have one that says mocp 25amps, so it has a 25a breaker in the panel (the panel is inside).
The only thing to watch for would be if the unit required FUSE protection and was not listed for a breaker protection. If that happened to be the case, you would need a fuse somewhere in the system. Otherwise non-fuse is fine as long as you have the required protection elsewhere,.