Condensing Unit disconnect

Status
Not open for further replies.

Stevedallas

Member
Location
Dallas, TX
Occupation
Engineer
I know 440 requires a disconnecting means. But, does it need to be fused?

I have one that says mocp 25amps, so it has a 25a breaker in the panel (the panel is inside).


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The only thing to watch for would be if the unit required FUSE protection and was not listed for a breaker protection. If that happened to be the case, you would need a fuse somewhere in the system. Otherwise non-fuse is fine as long as you have the required protection elsewhere,.
 