hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have condensing unit MCA: 24.9A, MOCP: 30A. The condensing unit has fused disconnect with fuse size of 30A.
The engineer has provided 40A feeder breaker feeding the condensing unit fused disconnect. The engineer has provided #10 awg feeder cable s feeding the unit fused disconnect.
Should the feeder cables be #8 awg not #10 awg?
The engineer has provided 40A feeder breaker feeding the condensing unit fused disconnect. The engineer has provided #10 awg feeder cable s feeding the unit fused disconnect.
Should the feeder cables be #8 awg not #10 awg?