Condit fill calculations
crtemp
Wa state
I'm confused on the tables and annex c part of the nec.
Say I have the following....
All THHN in a schedule 80 pvc
#12 x10
#10 x5
#8 x3
Since I have over 2 wires in one conduit do I calculate the cross sectional area of the conduit at 40% and then add up cross sectional area of each wire and add them up and see what size the Will fit into?
First start on Table 5 ch9
find THHN row and use Approximate area square inches.
then add the total of all of the conductors of your example.
Then go to raceway properties Table 4 of ch9
Find rigid PVC conduit
scroll down the 40% column until you find a number that is higher than the total area that you calculated.
then look to the left of that row you will see what conduit is needed.
Added: Based on my calculation you need a 1.25" conduit
That's pretty much what I was thinking. Thank you for the clarification. Does the annex c take the 40% into consideration when it states the maximum number of conductors in any given raceway?
A
Annex C is only used when all the conductors are the same size with the same insulation. It is based on the table for 1 wire (53%), 2 wires(31%) or over 2 wires (60%)
A
Annex C is only used when all the conductors are the same size with the same insulation. It is based on the table for 1 wire (53%), 2 wires(31%) or over 2 wires (40%)
Corrected.
Essentially, it represents about 70% of the conduit diameter filled with cable, if you were to pack the cables as tightly as possible. Since two circles have a lousy packing factor in a circle, the area fill percentage is significantly less for 2 wires. 1 circle obviously has a 100% packing factor in a circle, so its area fill percentage is high. Then when you look at 3+ circles in a circle, the packing factor takes off to a steady cruising value between 80% & 90%.
Wire totals to .2014 in sq and 3/4'' EMT is .213 in sq at 40%
Just want to make sure I'm not missing something.
You are correct. It is less than 40%, but not by much, 37.79%
Personally it would depend on the length and number of bends, but I would go with 1".
Ya for sure. It was super tight when I physically looked at the pipe and wire. After all the parts to do it in EMT I said forget it and just ran 1-1/4" pvc. Much easier.
#12 x10
#10 x5
#8 x3
there's an app for that.....