S slyblvd New member Feb 22, 2009 #1 what would be the MBJ of a 800a service fed with two parallel sets of 600kcmil conducters
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 22, 2009 #2 The answer is in 250.66. Let us know what you think. Welcome to the forum. :smile:
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Feb 22, 2009 #3 infinity said: The answer is in 250.66. Let us know what you think. Welcome to the forum. :smile: Click to expand... That is not really the correct code reference. In many cases you do end up there, but not this time.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 22, 2009 #4 don_resqcapt19 said: That is not really the correct code reference. In many cases you do end up there, but not this time. Click to expand... Yup, Don's correct. I missed the 600 kcmil. Try 250.28(D)(1).