I see lots of posts here on CSST, but I have a question regarding non-CSST metallic gas piping.
I often see home inspectors claim that in a system that has a furnace or other appliance connected to fuel gas distribution piping, there has to be an obvious visible bonding jumper etc installed.
My rub with this is that International Fuel Gas Code 310.1 SPECIFICALLY states that if the piping is connected to the appliance no additional bonding is needed.
HOWEVER. "piping" is a defined term in the IFGC. My argument is that the flexible connectors often seen are NOT considered "piping" in the IFGC, rather they are considered an appliance connector.
In my opinion for the bonding to be continuous throughout the gas piping system, the connectors should be jumpered around.
Am I crazy?
I often see home inspectors claim that in a system that has a furnace or other appliance connected to fuel gas distribution piping, there has to be an obvious visible bonding jumper etc installed.
My rub with this is that International Fuel Gas Code 310.1 SPECIFICALLY states that if the piping is connected to the appliance no additional bonding is needed.
HOWEVER. "piping" is a defined term in the IFGC. My argument is that the flexible connectors often seen are NOT considered "piping" in the IFGC, rather they are considered an appliance connector.
In my opinion for the bonding to be continuous throughout the gas piping system, the connectors should be jumpered around.
Am I crazy?