If you have a parallel feed in a single conduit feeding a motor and you increase the conductor size by 125% do you also need to adjust the conductor for more than 3 current carrying conductors in a conduit.
 
deerwood said:
If you have a parallel feed in a single conduit feeding a motor and you increase the conductor size by 125% do you also need to adjust the conductor for more than 3 current carrying conductors in a conduit.

Yes.