Re: conductor ampacity ambient temp derating
Sorry kralcp, but I do not follow your point. Let me first assert that the temperature of the conductor (i.e., the copper) means absolutely nothing in its own right. The only reason we care about the copper getting hotter is that it will, in turn, cause the insulation to get hotter. If you performed a laboratory experiment in which you continued to raise current (i.e., well beyond the NEC limits) until ?something happens,? that something is going to be an insulation something long before the copper undergoes the slightest change.
If you are running the NEC limited current through a 60C rated conductor in a 30C ambient, what you will not get is an insulation temperature above 60C. That means that there will be a temperature rise within the insulation system of 30C, and that it will have been caused by a temperature rise of more than 30C within the copper. Heat flows from the hotter area (i.e., the copper) to the cooler area (i.e., the insulation system). So yes, the copper is above 60C. But we do not care.
If you were then to raise the ambient by, let us say, 15 degrees, then the copper temperature will go above 75C, and the insulation system should approach, but not exceed, 75C. That would be a bad thing, since the insulation system is only rated for 75C. Therefore, we are required to reduce the current in the conductor, using the temperature correction factors associated with Table 310.16. This causes the temperature rise within the copper to be less, and results in a temperature of the insulation system that does not exceed its 60C rating.
Does this perspective help in any way, or do you still have a need for convincing?