I'm having a debate with some guys on the ampacity of some aluminum wire, although this question could cover other wire types as well. This particular installation is feeding a detached garage underground.
I'm looking at Southwire's mobile home feeder in this instance.
Here's straight from their specs:
"Southwire mobile home feeder consists of four quadruplexed type RHH or RHW-2 or USE-2 AlumaFlex TM AA-8000 series
aluminum alloy compacted conductors. The cable contains a triple extruded white striped neutral conductor and a green
grounding conductor to eliminate the need for field marking per the National Electrical Code. Insulation is sunlight resistant"
http://www.southwire.com/products/MobileHmFeeder.htm
The question is how do I determine which column to use? One person says I need to use the 60 degree column because it's USE, so it falls under 338.10(B)4(b) and then part II of art. 340 which limits it to 60 degrees. I thought since it was slash rated as RHH and RHW-2 as well this meant we take it straight from table 310.15(B)16?
But now I'm wondering, are we supposed to pick the insulation type based on how it's installed? Do you figure it's USE if it's direct buried while you can figure it as RHH/RHW-2 if it's installed in conduit?
Thanks.
I'm looking at Southwire's mobile home feeder in this instance.
Here's straight from their specs:
"Southwire mobile home feeder consists of four quadruplexed type RHH or RHW-2 or USE-2 AlumaFlex TM AA-8000 series
aluminum alloy compacted conductors. The cable contains a triple extruded white striped neutral conductor and a green
grounding conductor to eliminate the need for field marking per the National Electrical Code. Insulation is sunlight resistant"
http://www.southwire.com/products/MobileHmFeeder.htm
The question is how do I determine which column to use? One person says I need to use the 60 degree column because it's USE, so it falls under 338.10(B)4(b) and then part II of art. 340 which limits it to 60 degrees. I thought since it was slash rated as RHH and RHW-2 as well this meant we take it straight from table 310.15(B)16?
But now I'm wondering, are we supposed to pick the insulation type based on how it's installed? Do you figure it's USE if it's direct buried while you can figure it as RHH/RHW-2 if it's installed in conduit?
Thanks.