So after looking at this... After the correction factors, the wires from example on page 329 can carry 18 amps. And also a 16 amp continuous load requires a 20 amp rated wire and circuit breaker. The only thing I don't understand about David's response is that the load to be served is 20 amps, not 16(due to the fact it's is a continuous load)? So as I questioned before... Is the 125% of continuous load only considered on the wires actual ampacity before any correction factors are to be considered?
You are making an error here. The LOAD is 16A, not 20A. Lets say you had two loads, both 1920VA @ 120V, one which would be continuous, one which would be non-continuous.
BOTH circuits would have a load current of
16A. (The load that is continuous doesn't have a load current of 20A.)
Also MasterTheNEC said...
Branch-circuit conductors shall have an ampacity
not less than the maximum load to be served.
Read this sentence again..."shall have an
ampacity not less than the maximum load to be served." Again, the conductors need to have an ampacity of at least 16 to serve the load (whether the load is continuous or non-continuous.) Note that here they are talking about conductor
ampacity, where later they talk about conductor
size.
Conductors
shall be sized to carry not less than the larger of 210.19(A)(1)(a) or (b).
(a) Where a branch circuit supplies continuous loads or
any combination of continuous and noncontinuous loads, the
minimum branch-circuit conductor size shall have an allowable
ampacity not less than the noncontinuous load plus 125 percent
of the continuous load. This would be 16 * 1.25 which is = 20 amps
Note that here, they are talking about conductor
size. So what size conductor has an allowable ampacity of 20? Assuming the terminations are rated for 75 deg, #14 AWG has an allowable ampacity of 20. So for part (a) the minimum conductor size is #14.
(b) The minimum branch-circuit conductor size shall have
an allowable ampacity not less than the maximum load to be
served after the application of any adjustment or correction
factor. This would be the = 18 amps
So what size conductor would have an allowable ampacity of not less than 16 after the adjustment or correction factors have been applies? For THHN conductors, #14 AWG with the 0.6 adjustment factor would have an ampacity of 25*0.6=15...15 is less than the load current of 16, so it is too small. #12 AWG with the 0.6 adjustment factor would have an ampacity of 30*0.6=18. So for part (b) the minimum conductor size is #12.
The larger of these two is what
Branch-circuit conductors shall have an ampacity
not less than the maximum load to be served. Conductors
shall be sized to carry not less than the larger of 210.19(A)(1)(a) or (b)
would be the 20 amps?
?Please help me understand what I am not seeing here?
The larger conductor of the requirements of 210.19(A)(1)(a) or (A)(1)(b) is #12 Awg. That would be the minimum conductor size allowed.
Hope this makes sense.