When installing conductors in an underground duct bank how is the correct ampacity selected and or calculated? After looking at different factors like load factor, dielectric loss, power factor of the cables, etc. and looking at the nec and their duct bank installations it refers to ?one? or ?two? circuits. If you had parallel feeders let?s say six sets of parallel conductors, two individual loads requiring six sets now you have a duct bank in the orientation of 2 rows high and 6 rows wide with that being the case is this considered a two circuit duct bank even though there are 12 used ducts? There are only two circuits routed through the duct bank but with parallel feeders? Or is each conduit considered a circuit? Therefore you have 12 ducts being used in the 2x6 configuration that does not exist in the nec details. The cable ampacity calculations I have found refer to load factor, depth, and temperature not necessarily duct bank configuration outside of what is indicated in the NEC? 