Conductor ampacity is calculated in accordance with 310.15 based on 90?C conductor insulation rating, provided the adjusted or corrected ampacity doesn?t exceed that for a 60?C rated conductor.
Where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing that is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor must be adjusted in accordance with Table 310.15(B)(2)(a). Figure 334-3
Author?s Comment: This new requirement only applies to wood framing members, and has no effect unless you bundle more than nine current-carrying conductors together.
15A Circuit. If we bundle three 14/2 and one 14/3 cable (nine current-carrying 14 THHN conductors), the ampacity for each conductor (25A at 90?C, Table 310.16) is adjusted by a 70 percent adjustment factor [Table 310.15(B)(2)(a)].
Adjusted Conductor Ampacity = 25A x 0.70
Adjusted Conductor Ampacity = 17.5A
Question, how can you exceed the 60 degree C(from the adjusted ampacity)if your more than 9 current carrying conductors?
Example:11 current carrying conductors = 50%
25A x 0.50 =12.5<<<< how is that exceeding ??
[ August 30, 2005, 10:10 PM: Message edited by: nmbme ]
Where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing that is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor must be adjusted in accordance with Table 310.15(B)(2)(a). Figure 334-3
Author?s Comment: This new requirement only applies to wood framing members, and has no effect unless you bundle more than nine current-carrying conductors together.
15A Circuit. If we bundle three 14/2 and one 14/3 cable (nine current-carrying 14 THHN conductors), the ampacity for each conductor (25A at 90?C, Table 310.16) is adjusted by a 70 percent adjustment factor [Table 310.15(B)(2)(a)].
Adjusted Conductor Ampacity = 25A x 0.70
Adjusted Conductor Ampacity = 17.5A
Question, how can you exceed the 60 degree C(from the adjusted ampacity)if your more than 9 current carrying conductors?
Example:11 current carrying conductors = 50%
25A x 0.50 =12.5<<<< how is that exceeding ??