I'm working in Afghanistan, and NEC compliance is a huge issue here. Most of these camps are set up by the military, and have been constructed before our arrival, and it's up to us to try and meet code compliance where possible.
One issue is power distribution, and I'd like a little input on conductor ampacity rating and calculation as per 110.14(C)(1) as well as ampacity tables.
It is common practice here throughout all of the camps I've seen to use Type W single conductor cable, ampacity table T400.5(b). In regards to 110.14(C)(1), can I use the T.400.5(b) ampacity ratings where terminating to a 75 degree circuit breaker? Or am I being directed to apply the ampacity listed from T310.16?
Am I misreading or missing the intent of 110.14(C) completely?
Thanks
One issue is power distribution, and I'd like a little input on conductor ampacity rating and calculation as per 110.14(C)(1) as well as ampacity tables.
It is common practice here throughout all of the camps I've seen to use Type W single conductor cable, ampacity table T400.5(b). In regards to 110.14(C)(1), can I use the T.400.5(b) ampacity ratings where terminating to a 75 degree circuit breaker? Or am I being directed to apply the ampacity listed from T310.16?