Conductor and ocpd sizing for a/c heat unit

Status
Not open for further replies.

ctaylo360860

Senior Member
Location
colorado
Occupation
ME
I’m sure I’m overthinking this but wanted to make sure I didn’t miss anything nec wise. The unit shows 4800watts/240v=20amps on the plug. The books says nema 620-r receptacle. I planned on running a 240v circuit using 12-2nm and installing the 6-20receptacle
 

Attachments

  • 203709F2-9F50-4F50-9316-274F3B1700C1.jpeg
    203709F2-9F50-4F50-9316-274F3B1700C1.jpeg
    236.6 KB · Views: 9
  • C476E479-0541-4F91-A187-42027F1E76C8.jpeg
    C476E479-0541-4F91-A187-42027F1E76C8.jpeg
    341.8 KB · Views: 9

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I’m sure I’m overthinking this but wanted to make sure I didn’t miss anything nec wise. The unit shows 4800watts/240v=20amps on the plug. The books says nema 620-r receptacle. I planned on running a 240v circuit using 12-2nm and installing the 6-20receptacle
Can’t go wrong with the nameplate data.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That plug will only fit in a 240 volt, 20 amp receptacle so that is the configuration of the branch circuit that's required.
 