I HAVE 3PHASE WATER TRANSFER PUMP rating 93 KW , 380 , 60 HZ and the motor power consumption is 56 KW , my questions are :
1- the sizing to calculated for the pump rating (93kw) or for the consumption (56kw)
2- i belive that the design of the conductor/C.B must be based on the pum rating ; I= 93000/1.73*380*0.8 =176.6 A
THE CURRENT CARRYING CAPACITY OF THE CONDUCTOR MUST BE NOT LESS THAN 176.6 * 1.25 =220.75 A
and the C.B = 1.75 * 176.6 =309 A , THEN the C.B IS 325 A
PLEASE ADVICE FOR THE CORRECT WAY ACCORDING TO NEC
REGARDS FOR ALL