What is the 1.732 for? Thanks
Branch Circuit Continuous Load Example: What size branch-circuit overcurrent protection device and conductor (THHN) is required for a 19 kVA of nonlinear loads (75?C terminals). The branch-circuit is supplied by a 208/120 volt, 4-wire, 3-phase, Wye connected system.
Step 1 - Size the overcurrent protection device in accordance with Sections 210-20(a) and 384-16(d). The first thing that we must do convert the nonlinear load from kVA to amperes:
Amperes = VA/(Volts x 1.732), Amperes = 19,000/(208 volts x 1.732), Amperes = 52.74 amperes, rounded to 53 amperes
The branch-circuit overcurrent protection device must be sized not less than 125% of 53 amperes, 53 amperes x 125% = 66 amperes. According to Section 240-6(a) we must select a minimum 70 ampere overcurrent protection device.
Branch Circuit Continuous Load Example: What size branch-circuit overcurrent protection device and conductor (THHN) is required for a 19 kVA of nonlinear loads (75?C terminals). The branch-circuit is supplied by a 208/120 volt, 4-wire, 3-phase, Wye connected system.
Step 1 - Size the overcurrent protection device in accordance with Sections 210-20(a) and 384-16(d). The first thing that we must do convert the nonlinear load from kVA to amperes:
Amperes = VA/(Volts x 1.732), Amperes = 19,000/(208 volts x 1.732), Amperes = 52.74 amperes, rounded to 53 amperes
The branch-circuit overcurrent protection device must be sized not less than 125% of 53 amperes, 53 amperes x 125% = 66 amperes. According to Section 240-6(a) we must select a minimum 70 ampere overcurrent protection device.