Ok I need just alittle clarification on this topic. When correcting the ampacity of conductors either for ambient temp or more than 3 current carrying conductors bundled in raceway why do we use the 90C column for correction factors?
When sizing conductors this column cannot be used circuits rated 100A and less use the 60C column and circuits 100A and more use the 75C column (unless terminals are marked otherwise). So why do we use the 90C column for correction factors? And do we apply this correction factor to the correct size wire determined from the 60C and 75C column? Thanks
When sizing conductors this column cannot be used circuits rated 100A and less use the 60C column and circuits 100A and more use the 75C column (unless terminals are marked otherwise). So why do we use the 90C column for correction factors? And do we apply this correction factor to the correct size wire determined from the 60C and 75C column? Thanks