Terry Hoff
- Charleston SC
- Electrician
Does a conductors ampacity get reduced if you use the crimped barrel lug to fit under a terminal point?
I have not run into a case where the any reduced ampacity matteredDoes a conductors ampacity get reduced if you use the crimped barrel lug to fit under a terminal point?
That is correct, but if the lug is rated for 75C, then the conductor has to be rated at that temp also. It can’t be rated at 90C with a 75C lug.The crimped on barrel lug does nothing to reduce the ampacity of a conductor.
However, depending on the condition of the crimp, and, the resistance of that crimp ,if any, may cause a rise in the amperage of the circuit.
JAP>
How might a resistance increase current? Heat, yes, but a rise in current?However, depending on the condition of the crimp, and, the resistance of that crimp ,if any, may cause a rise in the amperage of the circuit.
Do you know where those solid pin adaptors would typically be used?Many of the crimp on reducers are not suitable for use with mechanical terminations. The terminations are typically only suitable for use with Class B and C stranded conductors. Many of the reducers have solid pins making them unsuitable for use with terminations that are only designed for use with Class B or C stranded conductors.