Conductor Derating and 90 degree column?

Status
Not open for further replies.

doof

Member
When you apply the derating factors in table 310.15.(B)(2)(a), can you start using the 90 degree column? Assuming 310.16, THHN and only 75 degree terminations. "They" told that it is allowed, but I cannot find where it is allowed and neither can "they".
Thanks!
 
Derating starts at the figures given in the table.

For instance, for #12 THHN copper, you start derating at 30. 310.15(B)
 
My understanding is that you have to use the _lowest_ temperature rating of everything connected in the region being considered.

If you have 90C wire connected to a 75C terminal, then at the point of that connection you need to use the 75C rating to determine ampacity

If somewhere else along the length of the wire it is subject to different surrounding conditions (say higher ambient temperature or derating for other current carrying conductors), then you use the temperature ratings of the components in that region. So the 90C conductor _in the conduit_ is derated from 90C, even though elsewhere it is connected to a 75C component.

Since the current is the same everywhere along the wire, the minimum ampacity determined at every point along the wire is the one that holds.

There is clearly a hole in this understanding, and I don't see an answer in the code: how much separation is required between 'regions'. Copper is a good conductor of heat; if the wire is at 90C inside the conduit (it likely is not, but it could get to that temperature), then how much wire is required before you hit the 75C termination.

-Jon
 
110.14(C)(1) is the equipment provisions I think is being discussed here.

It reads, in part, "...Conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.15(B)(6)."

If you are trying to derate conductors, start with the value given in T310.16 and modify them.
 
Last edited:
I think what the OP is looking for is something along the lines of what we see in 334.80:
The ampacity shall be in accordance with the 60?C (140?F)
conductor temperature rating. The 90?C (194?F) rating
shall be permitted to be used for ampacity derating purposes,
provided the final derated ampacity does not exceed
that for a 60?C (140?F) rated conductor.

However, the OP is using THHN - not NM.


110.14(C)(1) is where the derating/adjustment comes into play for THHN conductors.
 
doof said:
Can I use the 90 degree column, when derating for equipment only rated for 75 degrees?
No. You start with the 90C column only if you are using conductors rated for 90C. Look at the second sentence of 110.14(C), the sentence located just before subparagraph (1) begins.
 
doof said:
When you apply the derating factors in table 310.15.(B)(2)(a), can you start using the 90 degree column? Assuming 310.16, THHN and only 75 degree terminations. "They" told that it is allowed, but I cannot find where it is allowed and neither can "they".
Thanks!

You can start at the 90C for derating even though the terminations are rated 75C, however the OCPD cannot be any higher than the 75C-- art.110.14
 
Dennis Alwon said:
You can start at the 90C for derating even though the terminations are rated 75C, however the OCPD cannot be any higher than the 75C-- art.110.14


The same would apply if you were using NM cable which contains THHN conductors, only that the final adjusted ampacity cannot exceed the 60 degree C ampacity.
 