Under the various tables 310.XX there is a derating table for temperature that seems to indicate that wire ampacity is specified at 30C/86F. Then there are derating numbers for higher and lower temperatures. And we usually size at 125% in many applications under other articles. Similar tables and deratings appear in NFPA79 as well.
When or do you apply this other temperature derating? And what are we using for temperature, maximum expected or is this supposed to be an annual average?
Most attics can hit 140F. Most plants can hit >100F in the summer, especially in parts south. Most equipment is rated for 40-50C max operating environment.
Where called for, is the 125% rule expected to cover this temperature issue or not?
I may be missing something in the fine print. I prefer to err on the side of thicker, especially if I know it will be a continuous load in a very warm room, but it often gets annoyingly thick, sometimes thicker than the terminals can accept. I won't start a rant on UL listed 20A & 30A rated devices with 14AWG or smaller terminals here.
Matt
When or do you apply this other temperature derating? And what are we using for temperature, maximum expected or is this supposed to be an annual average?
Most attics can hit 140F. Most plants can hit >100F in the summer, especially in parts south. Most equipment is rated for 40-50C max operating environment.
Where called for, is the 125% rule expected to cover this temperature issue or not?
I may be missing something in the fine print. I prefer to err on the side of thicker, especially if I know it will be a continuous load in a very warm room, but it often gets annoyingly thick, sometimes thicker than the terminals can accept. I won't start a rant on UL listed 20A & 30A rated devices with 14AWG or smaller terminals here.