Conductor derating

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
If I am using 90 degree C #12 AWG insulation can I use the 30A in Table 310.16 for derating?


Sent from my iPhone using Tapatalk
 
I agree with Dave, I would add the one other scenario could be if the conductor was used in a wet location where THHN/THWN is only good for 75° C when wet. If it's THHN/THWN-2 your good either wet or dry.
 
Also nm cable would be at the 60C column not 75C
You need to take note of the asterisks after 10, 12, and 14 gauge and see the bottom of the table-- it directs you to 240.4(D)
 