jhaskins20018
Member
- Location
- Washington, DC
I am installing a Generac Standby 20KW Natural Gas Generator and it's Nexus Smart Switch is Service Rated for 200 amp as well as the existing Distribution panel. I know that this generator's maximum ampere output is 75 amps per phase and I have installed three number 1/0 thhn copper inside the Emt conduit as there is also a SOW 10-4 within the same conduit which is connected to a sub panel for future use to a proposed shed not constructed as of yet. I believe I have reached the maximum conduit fill and I need to run the equipment ground which I want to use number two green THHN copper which will be tied to the panel ground as well as the Transfer switch ground and terminated to a copper ground rod to earth. There seems to be a question in the NEC code for using SOOW or SOW in a EMT conduit and I want to run the equipment ground in a separate 3/4 inch pvc which will have a low voltage landscape 12 volt line enclosed. The control circuit is in a separate 3/4 in. PVC conduit to the transfer switch which the whole set up is single phase. Can this be done as I have described and be acceptable as per code?:?