Hey so I have a wire calculation issue. The contractor has 3” schedule 40 PVC with a fill rating at 40% is 2.907. The wire is #10 PV wire rated at 2000 volts with an outside diameter of .264. I think you have to solve for Cross sectional area of the PV wire which would be Pi times the radius squared. Then divide that number into the 2.907.... I come up with 26 conductors however the contractor is claiming he is allowed 50 conductors.