Conductor hash interpretation

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
How would you interpret the hash marks on the conduit runs in this picture? These particular runs are (2)120V circuits. Are the three hashes 2 hots + neutral and the separate hash is ground? Or do you think it's implying a third, spare hot, and the separate hash is the neutral--with the ground being either implied or the conduit? There is no legend for the conduit fills.
1721660536106.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You have to ask...in the past that would have been used for a 4 wire, multiwire circuit, but typically the neutral slash would have been a bit longer than the slashes for the ungrounded conductors.
 