Conductor min. voltage rating in starters

Status
Not open for further replies.

gsc

New member
Is there a article in the NEC that would require all wiring in a 480VAC motor starter to be 600VAC rated, including the wiring to a 24VDC coil or contact circuit as part of a motor control circuit?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Conductor min. voltage rating in starters

Yes, 2002 NEC 300.3(C)(1)

Here is part of it

All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure
 