This is probably a silly question, but I am curious if someone can provide me a definitive code reference for the following situation:
Branch-circuit load of 70A continuous (type of load not listed in 240.3).
Per 210.19, ampacity of conductors sized to 125% of continuous load (no ampacity adjustments applicable) / 70A * 1.25 = 87.5A.
Per 210.20, overcurrent protection shall not be less than 125% of continuous load / 70A * 1.25 = 87.5A.
Is there a specific code reference that defines the maximum size of conductors and OCPDs utilized?
My contention is that such a reference does not exist and that obvious factors affecting the maximum conductor / OCPD would be:
- Cost
- Lugs
- Load Requirements
Am I missing something here????
Branch-circuit load of 70A continuous (type of load not listed in 240.3).
Per 210.19, ampacity of conductors sized to 125% of continuous load (no ampacity adjustments applicable) / 70A * 1.25 = 87.5A.
Per 210.20, overcurrent protection shall not be less than 125% of continuous load / 70A * 1.25 = 87.5A.
Is there a specific code reference that defines the maximum size of conductors and OCPDs utilized?
My contention is that such a reference does not exist and that obvious factors affecting the maximum conductor / OCPD would be:
- Cost
- Lugs
- Load Requirements
Am I missing something here????