trafficmike

Member
Location
Seattle, WA
Good day all.

I am working on a roadway illumination project which contains some outlets on the poles. From my line loss calculations, I determined that I needed a #4 conductor. However, from the service cabinet breaker calculations, I determined I only need a 25A breaker. In the review, one comment was whether a #4 conductor can fit a 25A breaker. So, simple question, can it?

Thank you all in advance.

Mike
 

dicklaxt

Senior Member
There are some reduction end lugs that would have on one end a female opening for the #4 and the opposite end is a stud that terminates at/on the
breaker.I can't remember who makes them or the actual name but I specified a bunch of them for a job a couple of years ago.

dick
 