Re: Conductor size calculation- Motors
Hi Sparky.
I am not sure if I understand what you are asking here.
But it sounds to me you are asking if you need to size the conductors to the short circuit ground fault protective device.
If that is the question the answer is no.
430.52 is only for finding the size of the Motor Branch-Circuit Short-Circuit and Ground-Fault Protective Device.
Conductor sizing is based on the tables in the back of 430.
It is possible to be code compliant and have conductors connected to breakers that are rated much less than the breaker size.
An extreme case could have 14 awg on a 60 or 70 amp breaker.
The motor overload devices protect the conductors from being overloaded.
If that is not what you where asking sorry.
Bob