Hi Guys,
I'm trying to find some guidance in the NEC on a voltage reference tap and having trouble.
So, I'm working with a developer that has a load monitoring device (like an Emon Dmon) that they want to install in a customer's gear. The gear is a 3000A bus that goes has only a 3000A bus duct tapped off of it - there are no breakers for the circuit except for several floors up. Now, if I want to connect the voltage reference for the monitoring unit, I keep ending up at the 10ft tap rule. I would tap off the bus with 350kcmil (10% of 3000A is 300A...) and go to a 30A fused disconnect with 15A fuses. Then I'd connect the voltage reference for the monitor there...seems overkill for something that might pull 100mA at most.
However, we all know when you look inside gear we see customer monitoring units just tapped directly to the bus using #12 or #14 and either inline 600V fuses or some other UL508 mini circuit breakers. Anyway, I'm wondering in the code where it says you can use a greatly reduced wire size if it's for control or reference voltage or monitoring, or something along those lines?
Thanks.
I'm trying to find some guidance in the NEC on a voltage reference tap and having trouble.
So, I'm working with a developer that has a load monitoring device (like an Emon Dmon) that they want to install in a customer's gear. The gear is a 3000A bus that goes has only a 3000A bus duct tapped off of it - there are no breakers for the circuit except for several floors up. Now, if I want to connect the voltage reference for the monitoring unit, I keep ending up at the 10ft tap rule. I would tap off the bus with 350kcmil (10% of 3000A is 300A...) and go to a 30A fused disconnect with 15A fuses. Then I'd connect the voltage reference for the monitor there...seems overkill for something that might pull 100mA at most.
However, we all know when you look inside gear we see customer monitoring units just tapped directly to the bus using #12 or #14 and either inline 600V fuses or some other UL508 mini circuit breakers. Anyway, I'm wondering in the code where it says you can use a greatly reduced wire size if it's for control or reference voltage or monitoring, or something along those lines?
Thanks.