I have a cable from a VFD to a local motor disconnect that is routed underground in a duct bank of 6. Motor is 60 HP @ 460 V.
77 amps * 1.25 = 96.25 amps. If the cable wasn't routed in the duct bank and was above ground, the minimum cable size per Table 310.15(B)(16) is 3 AWG at 75C.
With 6 electrical ducts, the cable size is 1 AWG per Table B.310.15(B)(2)(7).
Since the cable from the local motor disconnect to the motor is entirely above ground, would this be considered a continuation of the cable in the electrical duct and 1 AWG would be used, or would it be considered separate and a 3 AWG would be used?