mstrlucky74
- NJ
We have to cut back and extend as existing panel(PP5) being relocated.The second graphic says existing, is the feeder changing in size?
It is a 200A MLO, so 200A worth of feeder unless of course the fuse is smaller and you can use smaller ampacity wire.
Yes, unless there is some type of future growth planned.Thanks Ron. If you have a OCPD( in a panel or gear) feeding another panel the conductors should be sized off the rating of the OCPD feeding the panel/gear, correct?