Can #2 copper go on a 125 amp breaker for a sub panel feed. #2 copper is rated for 115 amps, 115 is not a standard breaker so I can use the next highest, correct?
The sub panel is a Tesla gateway. Its going to feed a 60 amp EV charger, hot tub , water heater and another sub panel controlling basement lighting/basement bar.