Feel like this should be easy, but we are struggling to resolve in our office:
We have an existing winch motor system --
1hp, 120v, single-phase, 11.4amps nameplate. Manufacturer requested a 20amp circuit breaker, #12AWG conductors, which is what was installed.
If you have a look at Table 430.248 of NEC, though, code shows a motor like this to be 16FLA. I would expect to run #12AWG conductors with ground-fault and short-circuit protection device of 30amps or max 40amps.
Contractor wants to add a 1amp receptacle load onto the existing 20amp circuit. For the life of us, we cannot figure out how to calculate this. We don't typically combine motor and receptacle loads. Which section of the NEC shows this calculation? Can the 1amp load be added?