Hi, I'm a little confused on conductor sizing based on NEC 430.22 and NEC 430.122. NEC 430.122 is pretty straight forward that the branch LINE side conductors with a drive in place should be 125% of the drive input rating. First, is this the rated input or the 'seen input'? If my drive is over-sized, can I go with the efficiency of the drive with relation to the motor to get the 'seen input' current and use that?
Additionally, for sizing the LOAD side conductors, are these to be based on 430.122 as well or 430.22? If 430.22, how is it that a 60min motor should allow conductor sizes of 150% when continuous motor is 125%. This seems backwards. Thoughts?