Re: conductor sizing for gas bond
250.104(B) tells us to size using 250.122, and to bond where it may be energized. Presumedly, the only way for a gas pipe to become energized, would be via the branch circuit that supplies the utilization equipment connected to the gas pipe. If no utilization equipment using electricity is connected, then no bonding is needed. The FPN adds that bonding everything would be nice, but is not necessary.