I want to backfeed 40A PV microinverter system into a 125A MLO garage subpanel. The subpanel is fed by #8cu from a 40A breaker in a 200A bus/200A main MSP. The garage is detached and the #8cu is trenched about 100ft, so to avoid needing to upsize the trenched wire, I am hoping that if I add a 40A main breaker in the garage subpanel, the #8 feeder wire won't need to be changed out.
Quoting 2014 NEC 705.12(D)(2)(3)(b):"Where two sources, one a utility and the other an inverter,
are located at opposite ends of a busbar that contains loads,
the sum of 125 percent of the inverter(s) output circuit current
and the rating of the overcurrent device protecting the busbar
shall not exceed 120 percent of the ampacity of the busbar."
...which I am interpreting to mean that wire only needs to be sized #4 (40A PV + 40A utility / 1.2 = 67A = #4cu @ 75°) at the garage, and #8 is sufficient from garage to the MSP as long as the garage subpanel has a main OCPD. Am I interpreting this correctly? Trying to avoid re-trenching the garage feeders.
Quoting 2014 NEC 705.12(D)(2)(3)(b):"Where two sources, one a utility and the other an inverter,
are located at opposite ends of a busbar that contains loads,
the sum of 125 percent of the inverter(s) output circuit current
and the rating of the overcurrent device protecting the busbar
shall not exceed 120 percent of the ampacity of the busbar."
...which I am interpreting to mean that wire only needs to be sized #4 (40A PV + 40A utility / 1.2 = 67A = #4cu @ 75°) at the garage, and #8 is sufficient from garage to the MSP as long as the garage subpanel has a main OCPD. Am I interpreting this correctly? Trying to avoid re-trenching the garage feeders.