Conductor sizing for typical long residential branch circuit

Merry Christmas

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
I have to quote adding a branch circuit that feeds a residential outdoor outlet. The 1-way ckt distance is 150ft, and the receptacle will be 20A (GFCI) with a 20A breaker in the load center. Using Southwire calculator, with 123V source voltage, 12AWG conductor, and 150ft length, the voltage drop is calculated as 7.3%, and 114V at load, with an assumed 15A current draw. With 12A draw it is 5.9% and 115.8V. Would you quote 12AWG or upsize to 10AWG? The outlet will be just for convenience, may be used for small yard tools occasionally.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since this is just a convenience receptacle I would use #12 unless they're willing to pay for #10's.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
150' may be pushing the limit for probable GFCI nuisance tripping due to normal capacitive leakage current.
 