If I up size conductors for voltage drop from POCO to first disconnect can the balance from first disconnect to branch circuit panels be sized to the amperage of the loads of the individual panels or must the upsized conductors carry thru to the branch circuit panels? For reason of VD running 2 parallel 500kcmil AL to 400A meter/disconnect can I run from the disco to the 2 interior breaker panels two sets of 250kcmil AL one set to each panel, under 25ft from meter/disconnect to the interior panels?