In the past, my previous boss used Table 310.16 nationwide for an 3000A underground duct bank. On a specific project, we ran across an engineer that questioned the conductor ampacity.
I use ETAP for breaker coordination and it will also calculate the derated value of conductors. But if I were to design a conductor run and the NEC standards are selected and 'with grouping effect' active, ETAP doesn't allow the user to input 10 conduit bank. In the 'help', it says that NEC doesn't allow for grouping effects. If this is the case then what is the purpose of all the Tables B.310.15(B)(2)(1) through (10). For example, Table B.310.15(B)(2)(7) specific pupose appears to be derating based on the number conduits in a duct bank. Can anyone explain?
So say I have a 6 conduit bank at 480V, Table B.310.15(B)(2)(7) has figures to follow and, as you say, maybe so does Table 310.16. NEC also states that, in case they screwed up and have given multiple values or multiple ways to calculate something, always use the lower value.
Thanks for your responses!!