GeorgeB
ElectroHydraulics engineer (retired)
- Location
- Greenville SC
- Occupation
- Retired
We are supplying a small portable (wheels) hydraulic power unit (5HP, 460-3-60) to a customer who asked us to furnish a 40 foot long power cable for them to plug it into their plant welding receptacles. Our electrical equipment is a simple combination starter including control transformer for over temperature and under level switches in a 120 control circuit. We are NOT a UL approved facility. We don't consider this (perhaps wrongly) a "control panel".
These "welding" convenience receptacles are protected and wired for 60A and use a pin-sleeve dead connect system. They will put their plug on our cable.
At the 6.1A full load, and for cord coiling and storage convenience, I would not usually use a cable suitable for 60A. From purely an ampacity standpoint, 16AWG would be suitable ... we'd usually furnish 14AWG and a L16-20P expecting a matching receptacle.
I am puzzled by requirements here ... I can plug #18 lamp cords into a 20A receptacle at the desk, but ...
It's not the cost of the wire, it is the convenience ... SHOULD we furnish 6AWG SO cord? Or SHOULD we furnish something in between? What are the criteria?
These "welding" convenience receptacles are protected and wired for 60A and use a pin-sleeve dead connect system. They will put their plug on our cable.
At the 6.1A full load, and for cord coiling and storage convenience, I would not usually use a cable suitable for 60A. From purely an ampacity standpoint, 16AWG would be suitable ... we'd usually furnish 14AWG and a L16-20P expecting a matching receptacle.
I am puzzled by requirements here ... I can plug #18 lamp cords into a 20A receptacle at the desk, but ...
It's not the cost of the wire, it is the convenience ... SHOULD we furnish 6AWG SO cord? Or SHOULD we furnish something in between? What are the criteria?