Since you are a student, some of us prefer to teach you how to obtain answers yourself, rather than just providing the answer and teaching you nothing.shakabrah said:What is the limit on 8awg in 1" rigid?
Do you have an NEC codebook?shakabrah said:How many #8 THWN conductors will fit in 1" rigid conduit/
Your in the right area, but the wrong table... C.1 is for EMT. Look for the "rigid" table.shakabrah said:OK, What I've come accross is the following:
According to Table C.1 - 8awg THWN has a maximum of 9 conductors
Is this correct?
Thanks!
Incorrect. (Right table, wrong number)shakabrah said:oops . . .scratch that!
I found Table C.8 "Max number for Rigid Metal Conduit"
Looks like the number is 4. Can anyone give me some feedback?
Thanks
4 is the number for RHH, RHW, RHW-2.shakabrah said:Looks like the number is 4. Can anyone give me some feedback?
It was all you man!!!shakabrah said:ah . . .it's 9 again. I was pulling the number from the wrong type (RHW).
Thanks!!!!