Mr. Tuttle
- wisconsin
We are running a 200 amp sub panel outdoor for 6 - 3 ton a/c units. Can we run 4/0-4/0-#4-#4 feeder ? 1-20 amp gfci rec. at panel
That is correct however for the op's understanding, the OCPD may still be 200 amp as long as the load is under 180amps as Trevor stated. 240.4(B)For #4/0 Al your connected load would need to be 180 amps or less to use a 200 amp OCPD.
Yes, I think the connected load was 130 amps roughly. All 15SEER A/C units. Since this was all going to be piped in my concern was the neutral. We "only" needed a neutral for the 1-20 amp general purpose gfci for A/C's. No other branch circuits will ever be added to this panel. So, 2,400 watts or 20 amps on the neutral. I was curious as to what the smallest neutral that can be ran with that setup and egc to match.