To supply a 50 amp load (outdoor spa) a NM cable is run indoors from residential service panel to outdoor disconnect. 2008 NEC 334.80 requires that the NM cable ampacity be in accordance with the 60 degree C conductor temperature rating of 310.15. Therefore a minimum conductor size #6 cu would be required.
However, 2008 NEC 110.14 (C) (1) (a) (3) allows a minimum conductor size #8 cu if the conductor terminations are marked with the maximum temperature rating. All terminations from supply to load in this circuit are marked for 75 degree C wire.
How is the correct size of wire determined if, it is as it appears, either size wire could be used?
Thanks