What is the correct wire size for this installation?
If you install two 240v 30A receptacles and run conductors in same conduit, you have 4 current carrying conductors. That requires a derate to 80% IAW Table 310.15(B)(2)(a).
And you would normally select a size THHN 10 AWG for a single receptacle. IAW Table 310.16.
A 10 AWG at 75C is rated at 35A, but IAW your article Conductor Sizing and the National Electrical Code you would use the 60C column for 100A or less, well THHN is not listed in the 60C column of the ampacity charts.
So I would still use 75C column. And since 80% of 35 is only 28A this would require me to use 8AWG for this install.
But!
IAW Table 210.21(B)(2) Maximum Cord-and-Plug-Connected Load to Receptacle a 30A receptacle is only allowed to have a 24A load connected, the THHN 10 AWG derated at 80% to 28A is really a correct choice?
or is 8AWG still the correct choice?
If you install two 240v 30A receptacles and run conductors in same conduit, you have 4 current carrying conductors. That requires a derate to 80% IAW Table 310.15(B)(2)(a).
And you would normally select a size THHN 10 AWG for a single receptacle. IAW Table 310.16.
A 10 AWG at 75C is rated at 35A, but IAW your article Conductor Sizing and the National Electrical Code you would use the 60C column for 100A or less, well THHN is not listed in the 60C column of the ampacity charts.
So I would still use 75C column. And since 80% of 35 is only 28A this would require me to use 8AWG for this install.
But!
IAW Table 210.21(B)(2) Maximum Cord-and-Plug-Connected Load to Receptacle a 30A receptacle is only allowed to have a 24A load connected, the THHN 10 AWG derated at 80% to 28A is really a correct choice?
or is 8AWG still the correct choice?