Designer371141
Member
Can you apply the 90C ampacity of wire for sizing when your lugs are all only 75C rated, example; tri-plex XHHW cable, installed in duct bank, requirement is for 1000amps, the lead engineer is applying the 430 amp rating of the 90C in Article 310.15 and derating for 104F temperature to meet his needs, utilizing only three parallel runs. Is this