Hi Guys,

I'm stuck with this question, Could you please help me to get the right answer? Thank you.

The minimum size THWN Conductor that can be used on a 48amp load in a conduit with a total of 15 current-carrying conductors is ___AWG.

A)8 B)2 C)3 D)4

My answer is 48x 0.50=24 #12 obviously is not the correct answer. looking forward for your help. Thank you.
 

shaxruz1991

Member
Location
New York
06075b792861b49f04a97d14022c1ca7.png



Sent from my iPhone using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
And the correct answer is #1 awg

We don't know the terminations and the load is less than 100 amps so we have to assume 60C per 110.14(C). #2 at 60C is 95 amps. Thus we need to go to #1.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Just going by what is available here. Nothing but THWN-2, don't know when I've seen just TWHN. But since the question specifically mentioned THWN, I guess you're correct.
I hear you. Then OP sounds like a test or homework question so the THWN part is relevant.

#1 AWG is not on the list of choices. :)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I hear you. Then OP sounds like a test or homework question so the THWN part is relevant.

#1 AWG is not on the list of choices. :)


I know it is not but that is the correct answer. Of course, the instructor is looking for #2 but he needs to give more info for that.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
And the correct answer is #1 awg

We don't know the terminations and the load is less than 100 amps so we have to assume 60C per 110.14(C). #2 at 60C is 95 amps. Thus we need to go to #1.
Dennis, you could use the 75 deg column for derating since the conductors are THWN. 115A x 50%=57.50A
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Why can you use the 75C?

(a) Termination provisions of equipment for circuits
rated 100 amperes or less, or marked for 14 AWG through
1 AWG conductors, shall be used only for one of the following:
(1) Conductors rated 60°C (140°F).
(2) Conductors with higher temperature ratings, provided
the ampacity of such conductors is determined based on
the 60°C (140°F) ampacity of the conductor size used.
(3) Conductors with higher temperature ratings if the equipment
is listed and identified for use with such conductors.
(4) For motors marked with design letters B, C, or D, conductors
having an insulation rating of 75°C (167°F) or higher
shall be permitted to be used, provided the ampacity of
such conductors does not exceed the 75°C (167°F)
ampacity.
 