That is why I stated if all the equipment was rated 75C. Good thing Trevor had experience with that particular device...So I checked the GE 50A Inlet box and its only rated for 60Deg conductors so i will use #6 for the Hots and neutral and a #10 for the ground. So 3-#6 at .0507 = .1521 + .0211 =.1732 which will still fit in a 3/4" Emt.
Thanks for reminding me of the rating of inlet box
The 50 amp Generac inlet I installed several years ago had only 60° C terminals. I had run #8 MC cable that was left over from a job and ended up having to install a junction box adjacent to the inlet to pigtail off the inlet with #6's. Basically this was a marine inlet in an enclosure for a generator connection. Now I only use the ones with the pigtails.